Measuring server energy efficiency


Dan Diesso, Contributor
05.16.2006
Rating: -4.00- (out of 5)


Digg This!    StumbleUpon Toolbar StumbleUpon    Bookmark with Delicious Del.icio.us   


Increasing power densities and soaring energy costs make measuring the energy efficiency of servers more important than ever. Obtaining these metrics requires the proper tools and methods to achieve accurate results.

Many people attempt to measure power using an amp meter. There are two problems with this approach.

First, power is measured in watts not amps. Watts = amps x volts x power factor. Attempting to use an amp meter to measure power forces to you guess at the voltage and power factor of the circuit creating the potential for considerable error.

The second problem is both amps and watts are instantaneous measurements. Even an accurate power measurement still only tells you about a servers "performance" at that particular moment.

To accurately measure a server's efficiency while running benchmark tests you need to measure the cumulative power consumption over the entire test. Cumulative power consumption over time is an energy metric measured in watt-hours. For this you need an electric watt-hour meter. Watt-hour meters are designed to continuously monitor the amperage, voltage and power factor of a circuit to accurately determine the true energy usage. Once you have energy measurements for various servers running the same benchmark tests you have way to compare the workload achieved for the amount of energy consumed.

There are a few important things to consider when choosing an appropriate watt-hour meter. One is the resolution of the meter. Many watt-hour meters are intended to monitor large loads over long periods of time and accumulate their readings in kWh (kilowatt-hours). This means the accumulator only increments each time there is 1,000 wat...


BROWSE BY TAG
Data center power management,   Data center design and infrastructure,   Data center power consumption and savings,   Infrastructure Management Tips,   VIEW ALL TAGS

Digg This!    StumbleUpon Toolbar StumbleUpon    Bookmark with Delicious Del.icio.us   



RELATED CONTENT
Data center power consumption and savings
Sizing computer room air conditioners for data center energy efficiency
IBM VMworld news in brief
Air-side and water-side economizers in the data center
How to choose the right uninterruptible power supply for your data center
Avoid common pitfalls when calculating data center power load
Amazon data center facility engineer touts radical cooling tactics
The TPC Energy Specification: Energy consumption vs. performance and costs
Measuring data center energy consumption in watts per logical image
Data center managers plan for power density jumps
Backup power in a shipping container: Active Power's PowerHouse

Infrastructure Management Tips
Grow a green business: Cut costs and improve energy efficiency with green IT
Closing the green gap: Expanding data centers with environmental benefits
Green data center site selection: Cost versus sustainability
Improving data center cooling capacity with chilled water plants
How to prepare for remote data center maintenance trips
DC Pro: a breakdown of a data center efficiency tool
Selecting a general contractor: Data center construction runbook, Chapter 3
Selecting a winning data center design team: Data center construction runbook, Chapter 2
Protecting your data center from real show-stoppers: Preparing a disaster recovery plan
Economizer performance: Applying CFD modeling to the data center's exterior

RELATED GLOSSARY TERMS
Terms from Whatis.com − the technology online dictionary
power usage effectiveness (PUE)  (SearchDataCenter.com)

RELATED RESOURCES
2020software.com, trial software downloads for accounting software, ERP software, CRM software and business software systems
Search Bitpipe.com for the latest white papers and business webcasts
Whatis.com, the online computer dictionary


t-hours of energy usage. Attempting to use such a low-resolution meter on smaller circuits over short periods is like using a calendar to measure a 100-yard dash. A high-resolution meter that measures in watt-hour resolution or better is needed for this type of application.

Watt-hour meters come in many form factors. Some meters can simply be plugged inline between the load and source using standard plugs and receptacles. Other meters require you tap into the circuit to obtain the voltage measurements and clamp a current transformer around a conductor of the circuit to obtain the amperage measurements. There are also branch circuit watt-hour metering systems available that can measure the energy usage of each individual circuit within a power distribution unit.

A functional consideration is that some watt-hour meters provide network connectivity for automated reading while others require reading them visually from a digital display. A big advantage of meters with network connectivity is you can easily log a series of readings for trending and analysis.

Power and energy measurements are important metrics for data center operators today. In addition to determining equipment efficiency these metrics also indicate heat loads to assist with cooling management. Energy measurements can also be used to allocate energy costs to those responsible for their consumption creating an ongoing incentive to deploy energy efficient equipment.

About the author:Diesso has been involved in the development and deployment of automated metering solutions for over 10 years and is the founder of Smart Works, Inc which provides power and environmental metering solutions to data centers.

Rate this Tip
To rate tips, you must be a member of SearchDataCenter.com.
Register now to start rating these tips. Log in if you are already a member.




DISCLAIMER: Our Tips Exchange is a forum for you to share technical advice and expertise with your peers and to learn from other enterprise IT professionals. TechTarget provides the infrastructure to facilitate this sharing of information. However, we cannot guarantee the accuracy or validity of the material submitted. You agree that your use of the Ask The Expert services and your reliance on any questions, answers, information or other materials received through this Web site is at your own risk.



White Papers - Data Center Networking

The Intel IT Technology Center - Power, Performance and Mobility Solutions

HomeNewsTopicsITKnowledge ExchangeTipsBlogsMultimediaWhite PapersEvents
About Us  |  Contact Us  |  For Advertisers  |  For Business Partners  |  Site Index  |  RSS
SEARCH 
TechTarget provides technology professionals with the information they need to perform their jobs - from developing strategy, to making cost-effective purchase decisions and managing their organizations' technology projects - with its network of technology-specific websites, events and online magazines.

TechTarget Corporate Web Site  |  Media Kits  |  Site Map




All Rights Reserved, Copyright 2005 - 2009, TechTarget | Read our Privacy Policy
  TechTarget - The IT Media ROI Experts