Cooling blade servers


Robert McFarlane
04.27.2006
Rating: -4.50- (out of 5)


Digg This!    StumbleUpon Toolbar StumbleUpon    Bookmark with Delicious Del.icio.us   


How much air movement does each blade server typically need for cooling?

When all manufacturers follow the ASHRAE Guidelines for listing power and cooling requirements, this will be an easy answer for anyone to obtain. I suggest you check with the manufacturer of your servers before going by "rules of thumb". However, since you asked for "typical requirements", the following may help.

Air quantity (Cubic Feet per Minute, or "CFM") is determined by three things: the Wattage draw of the equipment; the entering air temperature; and the heat rise you are willing to accept as the air goes through the equipment. Without getting into the technicalities of air conditioning, wattage is converted to heat at the rate of 3.4 BTU per watt. (BTU=watts x 3.4). The heat rise is the temperature differential between the air entering and the air leaving the equipment, and is simply called "TD". The formula for air quantity is:

CFM = BTU / TD x 1.08 (The 1.08 correction factor can be ignored for small calculations if you want.)

Common numbers for Blade Servers would be:

This is based on a good under-floor air system with the blade center near the bottom of the cabinet, where the cold air comes up from the floor. It also assumes that all spaces above and below it are filled with other equipment or blank panels to prevent...


BROWSE BY TAG
Data center design and infrastructure,   Data center power management,   Infrastructure Management Tips,   Data center design and infrastructure,   Cooling blade servers and high density servers,   Chapter 3: Data center cooling,   VIEW ALL TAGS

Digg This!    StumbleUpon Toolbar StumbleUpon    Bookmark with Delicious Del.icio.us   



RELATED CONTENT
Data center power management
Backup power in a shipping container: Active Power's PowerHouse
U.S. Bowling Congress moves data center, halves energy costs
Tom Friedman to data centers: 'Get ready for carbon tax'
Google opts for battery backup over UPS: News in brief
CRG West preps data centers for cloud computing customers
ViaWest data centers go green, which makes dollars and cents
Common data center hurdles: Cooling and power distribution problems
Data center power consumption: Key theme at DCD
Data center managers face mountains of technology shifts
Welsh data center expected to be Europe's most advanced
Data center power management Research

Infrastructure Management Tips
Grow a green business: Cut costs and improve energy efficiency with green IT
Closing the green gap: Expanding data centers with environmental benefits
Green data center site selection: Cost versus sustainability
Improving data center cooling capacity with chilled water plants
How to prepare for remote data center maintenance trips
DC Pro: a breakdown of a data center efficiency tool
Selecting a general contractor: Data center construction runbook, Chapter 3
Selecting a winning data center design team: Data center construction runbook, Chapter 2
Protecting your data center from real show-stoppers: Preparing a disaster recovery plan
Economizer performance: Applying CFD modeling to the data center's exterior

Cooling blade servers and high density servers
Cooling high-density racks
Egenera rolls out new blades, liquid cooled chassis
Blades in your data center?
Heat relief for data centers using blades
Will consolidating onto blades reduce heating loads?

RELATED GLOSSARY TERMS
Terms from Whatis.com − the technology online dictionary
Electric plugs for each country  (SearchDataCenter.com)
green data center  (SearchDataCenter.com)

RELATED RESOURCES
2020software.com, trial software downloads for accounting software, ERP software, CRM software and business software systems
Search Bitpipe.com for the latest white papers and business webcasts
Whatis.com, the online computer dictionary


warm "bypass air" from getting from the rear of the equipment back to the front and raising the incoming air temperature. If the blade center is mounted toward the top of the cabinet, the entering air temperature will have risen by the time it gets up there, perhaps to 75°F. In this case, either the equipment will tolerate a 95°F discharge temperature (20° TD), or you'll need more air to cool it.

Of course, this assumes that the tiny fans in the servers can actually move 840 CFM of air through the equipment. This is one of the reasons some manufacturers are specifying higher operating temperatures, and allowing 25° to 30° TD's. However, even if the specs say higher temps are OK, you can be sure the life of the hardware will be shortened, and that unexplained errors may very well be temperature related. And remember, a standard 25% open perforated tile, under normal "good" conditions (0.1" static pressure), can only pass about 675 CFM of air. Usually you'll get more like 500 CFM. Its not just the capacity of the air conditioners that counts – it's the air that actually gets to your technology.

Hopefully, this will help you determine what you need, whether or not your data center can provide it, and will also keep those expensive servers from burning up or shutting down at inopportune times.

Rate this Tip
To rate tips, you must be a member of SearchDataCenter.com.
Register now to start rating these tips. Log in if you are already a member.




DISCLAIMER: Our Tips Exchange is a forum for you to share technical advice and expertise with your peers and to learn from other enterprise IT professionals. TechTarget provides the infrastructure to facilitate this sharing of information. However, we cannot guarantee the accuracy or validity of the material submitted. You agree that your use of the Ask The Expert services and your reliance on any questions, answers, information or other materials received through this Web site is at your own risk.



White Papers - Data Center Networking

The Intel IT Technology Center - Power, Performance and Mobility Solutions

HomeNewsTopicsITKnowledge ExchangeTipsBlogsMultimediaWhite PapersEvents
About Us  |  Contact Us  |  For Advertisers  |  For Business Partners  |  Site Index  |  RSS
SEARCH 
TechTarget provides technology professionals with the information they need to perform their jobs - from developing strategy, to making cost-effective purchase decisions and managing their organizations' technology projects - with its network of technology-specific websites, events and online magazines.

TechTarget Corporate Web Site  |  Media Kits  |  Site Map




All Rights Reserved, Copyright 2005 - 2009, TechTarget | Read our Privacy Policy
  TechTarget - The IT Media ROI Experts